Thanks for reply’s does it matter f I use a 3kw element thanks andy
3kw divided by 240v not 220 so just within 13 amps.However if you go 3kw I would get an electrician to install a separate supply rather than a spur and to fit 16amp caravan type sockets.I did thus for a few years but on my current element dropped to 2kw as it let's you run a light or a battery charger off the same lead/socket and let's me retain normal 13a plugs.
3kw divided by 240v not 220 so just within 13 amps.
Quote from: AuRavelling79 on January 09, 2021, 08:05:30 pm3kw divided by 240v not 220 so just within 13 amps.UK supply used to be 240vac but with EU harmonisation in 1994 we changed to be more inline with Europe. The harmonisation was completed in January 2003.I believe UK supply is actually more like 230vac nominally. The point I was trying to make was it's not a good idea to run a 3Kw immersion heater of a 13 amp socket!